Normally open or closed?

Joined
10 Feb 2007
Messages
1,396
Reaction score
42
Location
Cumbria
Country
United Kingdom
Just purchased this contactor and it seems like a N-O contactor?
It is open circuit across all terminals.
What do you think?
20211016_145725.jpg
20211016_145757.jpg
 
It is open circuit across all terminals.
[URL='https://www.electrical2go.co.uk/memshield-3-20a-2no-230vac-contactor-cr2020230a.html']It will be open circuit across any combination of terminals with the exception of A1 to A2 ( the ends of the coil )
Only when there is 230 volts AC applied to A1 and A2 will

Terminal 1 be connected to terminal 2
Terminal 3 be connected to terminal 4


Eaton MEM CR2020230A 20A MOD Contactor 2NO 230VAC
https://www.electrical2go.co.uk › memshield-3-20a-2n...[/URL]
Eaton MEM CR2020230A 20A MOD Contactor 2NO 230VAC
CR2020230A ... A 2 Normally Open 20 Amp 230v AC Contactor, sized to a standard 18mm module width
 
It will be open circuit across any combination of terminals with the exception of A1 to A2 ( the ends of the coil )
Only when there is 230 volts AC applied to A1 and A2 will

Terminal 1 be connected to terminal 2
Terminal 3 be connected to terminal 4


Eaton MEM CR2020230A 20A MOD Contactor 2NO 230VAC
https://www.electrical2go.co.uk › memshield-3-20a-2n...

Eaton MEM CR2020230A 20A MOD Contactor 2NO 230VAC
CR2020230A ... A 2 Normally Open 20 Amp 230v AC Contactor, sized to a standard 18mm module width
What ohms should I expect from the coil?
 
What ohms should I expect from the coil?
The resistance of the coil when measured with DC test equipment will be very low compared to the operating impedance when a 50 Hz mains voltage is applied to the coil. I cannot find any information about DC coil resistance values for AC coils
 
I think you should expect whatever it turns out to measure. The chances of a new one being broken are extremely low.
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back