Hi all i recently had a issue with my electrical ring main I plugged in a appliance and it tripped the 32 amp associated to that ring. i reset the trip and noticed that there was no power to any sockets but did not tripping again.
The non-contact "pen-tester" indicated that there is Voltage in one of the conductors at the (SOCKET) point where you "tested".
It did not indicate "Current" (of which there was none)
and
it did not indicate that the Neutral (Return-Current Path) was still "intact".
There is very little on that ring a television and a router and maybe at times a mobile phone charger.
I thought the problem may be a faulty breaker so swapped it with another on the board but same problem is present any help would be appreciated
So, the TV, Router and Charger are no longer being supplied.
Hence, either the Line, Neutral (or both) supplying them is Open-Circuit.
To test whether the Line or Neutral connection is Open-Circuit
you need to use a (preferably, Low Impedance) Volt Meter,
in the proper manner -
at the many possible points on the "Ring".
Ok. It’s easy from here. Check the neutral cables that go with the lives that are in the MCB. Make sure those neutrals are securely connected in the correct neutral busbar
The all you have to do (!) is trace the cables and find out where the voltage is disappearing to.
Start in the middle of the ring and take wires out of the socket. You should see volts between L&N on both cables.
Firstly. You do not get current until there is a load attached. If you are testing with the MCB on then you are looking for voltage
Secondly. If you go not understand that very basic point then the only safe way to do these tests is by using a continuity tester, and with the circuit connections completely removed from the CU
BUT, thirdly - and with respect - I really can see no prospect of you being able to carry out this fault finding process. Please get an electrician to help.
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local