My tenant reported the NSH not heating, there is only one and not yet a year old.
My initial tests during the day, so no cheap rate, found the circuit between CU (E7 tail) and NSH terminals, via 20A DP switch, tested OK using the pictured meter on Ω range.
Next thing I needed was power so added a wire link to CU to bypass E7 contactor and expected to see a 3.3KW load... nothing.
The 20A switch prooved to be HR... more MK junk.
Replaced and straightaway meter beeped rapidly indicating overload on 40A range when power applied... Instant reaction?... Ooops. On 400A range I saw 82.8A
However half a second of thought later...
My initial tests during the day, so no cheap rate, found the circuit between CU (E7 tail) and NSH terminals, via 20A DP switch, tested OK using the pictured meter on Ω range.
Next thing I needed was power so added a wire link to CU to bypass E7 contactor and expected to see a 3.3KW load... nothing.
The 20A switch prooved to be HR... more MK junk.
Replaced and straightaway meter beeped rapidly indicating overload on 40A range when power applied... Instant reaction?... Ooops. On 400A range I saw 82.8A
However half a second of thought later...