Got a good one today.
Floodlight on unprotected side of S/L board trips RCD when switched on.
No neutrals crossed.
Find NE short on GF ring, along with no neutral continuity. But, when the "good" leg of the ring was re-instated, all sockets worked.
Came to the conclusion that the NE short must be "supplying" the return feed in place of the neutral.
Any other ideas?