Got a faulty 2.5 RF circuit today.
Tripping 32A CB, sometimes instantly, sometimes after 10 mins or so. No RCD protection. Suspect water ingress.
Disconnect all appliances from all known sockets.
Meg the circuit. 420 Ohm LE, 0 Ohms NE.
Suspect something still in circuit.
Find a cable still connected via fused unswitched spur which reads down NE. May be faulty, may just be something on the end of it. Cannot locate other end of cable.... Disconnect.
Still down!
Test ring continuity. Live - 0.86. Neutral 1.54
Split the ring. Meg circuit. One faulty leg, one healthy.
Reconnect healthy leg: All sockets now working.
Not sure if I've struck lucky and just happened to open up the socket with the first (or last) leg going to it OR there are more outlets I can't locate & one has an appliance plugged into it, this being the "faulty" leg.
Here are the other things I am stumped on:
1. Would an NE short on PME without RCD protection trip a CB? Having found faults in the past where N & E are shorted together and the circuit works without tripping, I can't quite understand this.
2. What explains the huge difference in the L & N ring continuity readings? AFAICS, all cabling is 2.5.
Tripping 32A CB, sometimes instantly, sometimes after 10 mins or so. No RCD protection. Suspect water ingress.
Disconnect all appliances from all known sockets.
Meg the circuit. 420 Ohm LE, 0 Ohms NE.
Suspect something still in circuit.
Find a cable still connected via fused unswitched spur which reads down NE. May be faulty, may just be something on the end of it. Cannot locate other end of cable.... Disconnect.
Still down!
Test ring continuity. Live - 0.86. Neutral 1.54
Split the ring. Meg circuit. One faulty leg, one healthy.
Reconnect healthy leg: All sockets now working.
Not sure if I've struck lucky and just happened to open up the socket with the first (or last) leg going to it OR there are more outlets I can't locate & one has an appliance plugged into it, this being the "faulty" leg.
Here are the other things I am stumped on:
1. Would an NE short on PME without RCD protection trip a CB? Having found faults in the past where N & E are shorted together and the circuit works without tripping, I can't quite understand this.
2. What explains the huge difference in the L & N ring continuity readings? AFAICS, all cabling is 2.5.