Hi guys.
I have had to deal with two faults recently that rather stumped me, but both solutions turned out to be incredibly simple. I shall explain each problem:
Fault 1.
Incomer RCD (30mA) on PME tripping when any upstairs light is switched on, but never immediately. Sometimes it takes several minutes. Water ingress and cable damage eliminated as cause. EFLI's at fittings very low.
Fault 2.
"16th edition" split-load board with one 30mA RCD on TT supply with Ze of 58.5 Ohms.
Tested hall light EFLI: 0.99 Ohms.
Tested EFLI at lounge light switch: 20.72 Ohms.
Turned hall light on, Metrel now showing RP.
Turned hall light off, Metrel now showing correct polarity.
Lighting on incomer side, not RCD protected.
I have had to deal with two faults recently that rather stumped me, but both solutions turned out to be incredibly simple. I shall explain each problem:
Fault 1.
Incomer RCD (30mA) on PME tripping when any upstairs light is switched on, but never immediately. Sometimes it takes several minutes. Water ingress and cable damage eliminated as cause. EFLI's at fittings very low.
Fault 2.
"16th edition" split-load board with one 30mA RCD on TT supply with Ze of 58.5 Ohms.
Tested hall light EFLI: 0.99 Ohms.
Tested EFLI at lounge light switch: 20.72 Ohms.
Turned hall light on, Metrel now showing RP.
Turned hall light off, Metrel now showing correct polarity.
Lighting on incomer side, not RCD protected.