Its a TT supply with 100mA time delay incomer RCD, and ordinary 30mA RCD. The lights and cooker are on on the 100mA RCD side of the board, and the sockets on the 30mA side. I installed the board to replace a rewirable months back. All insulation tests >500M at the time. I got called back as they started to get a lot of nuisance tripping (of the time delay RCD) when using cooker, kettle, toaster etc. I subsequently tested and found a N-E fault (40ohms) on the upstairs lighting circuit, and with this disconnected everything is fine. I was not able to find any obvious faults in any roses/switches or fittings, but they have had rats in the loft which is overboarded so could even be a gnawed cable. What is strange about the fault is that the 100mA RCD only seems to trip (with lighting circuit connected) when you power on the cooker and items on the sockets side, which as I said on on a different RCD. There are no crossed neutrals in the board either.
I've got to go back and try and localise the fault, by breaking down the circuit, unless anyone can suggest a better method, but can't fathom why there seems to be a relationship between the two sides of the board ?
I've got to go back and try and localise the fault, by breaking down the circuit, unless anyone can suggest a better method, but can't fathom why there seems to be a relationship between the two sides of the board ?