Often seen posted on various websites re above running out of hot DHW rapidly, and ditto with Gas fired Combis. Oil fired combis have stored primary water which I suppose is a must since they don't modulate and would result in the DHW running hot & cold due to the boiler cycling if the DHW demand is below the thermal output of the boiler.
I've built a spreadsheet below based on a 21kW Firebird Combi which I believe has a 35/40L store (I've used 35L) with a stored temperature of 75C, the calcs (if correct) show, assuming DHW temp of 45C, that in winter with a pretty low mains of 5C, dT (45-5), 40C that the maximum continuous flowrate is 7.4LPM but should sustain a flowrate of 13.7LPM for 10 minutes before the DHW temp starts falling off. At a present mains temp of 18C then those numbers should be 11.2LPM continuous and 18.5LPM for 10 minutes.
Has anyone monitored the flowrates of their oil fired boilers which might reflect the above, the spreadsheet numbers can easily be changed to reflect any oil fired combi, output, store vol and stored temperature, DHW setpoint temperature etc.
I've built a spreadsheet below based on a 21kW Firebird Combi which I believe has a 35/40L store (I've used 35L) with a stored temperature of 75C, the calcs (if correct) show, assuming DHW temp of 45C, that in winter with a pretty low mains of 5C, dT (45-5), 40C that the maximum continuous flowrate is 7.4LPM but should sustain a flowrate of 13.7LPM for 10 minutes before the DHW temp starts falling off. At a present mains temp of 18C then those numbers should be 11.2LPM continuous and 18.5LPM for 10 minutes.
Has anyone monitored the flowrates of their oil fired boilers which might reflect the above, the spreadsheet numbers can easily be changed to reflect any oil fired combi, output, store vol and stored temperature, DHW setpoint temperature etc.