Morning all
I've recently moved into the first house I've owned, built in about 1975, and am discovering the joys of ownership vs renting.
The house had an electric shower fitted when we moved in. While I was using it the other day the isolation switch went bang - inside the wires were all charred. Did a bit of investigating of the electrics for the first time.
The shower is wired to its own separate consumer unit, specifically a Memera one. It takes cartridge fuse, and the cartridge is stamped 30A. This didn't quite ring true for our shower which is 9.5kW and sure enough it wasn't a fuse inside, but a length of what I'm hoping at least was fuse wire, which had obviously blown.
This is a picture of the 3 consumer units which make up the system:
http://farm3.static.flickr.com/2414/2177176263_464134578f_o.jpg
And this is a picture of the unit the shower is wired to, and one of the cartridge which goes into it:
http://farm3.static.flickr.com/2365/2177968012_4eec5b8903_o.jpg
http://farm3.static.flickr.com/2246/2177968364_ef554d296f_o.jpg
The angle blocks some of the wiring (sorry!) but you can just about see the Memera shower CU also connects to this other Wylex one:
http://farm3.static.flickr.com/2075/2177968086_eac65e5025_o.jpg
The other 3-way CU is for the lights and sockets.
Two questions then really:
a) with apologies for my ignorance, what's the Wylex CU that the Memera one is connected to actually for?
b) is there any way of salvaging what's already there for the shower? I'm guessing not as 45A fuses don't seem to exist for Memera stuff, even if it wasn't stamped 30A - god knows what the wire was in there before! If not, do I need to replace it with something like this?
http://www.screwfix.com/prods/69659...nits/Volex-Shower-Unit-63A-30mA-RCD-1x50A-MCB
And if so, is doing that one of those notifiable things I read so much about on here?
If you need any more info please ask...
Any other useful advice also welcome... cheers!
I've recently moved into the first house I've owned, built in about 1975, and am discovering the joys of ownership vs renting.
The house had an electric shower fitted when we moved in. While I was using it the other day the isolation switch went bang - inside the wires were all charred. Did a bit of investigating of the electrics for the first time.
The shower is wired to its own separate consumer unit, specifically a Memera one. It takes cartridge fuse, and the cartridge is stamped 30A. This didn't quite ring true for our shower which is 9.5kW and sure enough it wasn't a fuse inside, but a length of what I'm hoping at least was fuse wire, which had obviously blown.
This is a picture of the 3 consumer units which make up the system:
http://farm3.static.flickr.com/2414/2177176263_464134578f_o.jpg
And this is a picture of the unit the shower is wired to, and one of the cartridge which goes into it:
http://farm3.static.flickr.com/2365/2177968012_4eec5b8903_o.jpg
http://farm3.static.flickr.com/2246/2177968364_ef554d296f_o.jpg
The angle blocks some of the wiring (sorry!) but you can just about see the Memera shower CU also connects to this other Wylex one:
http://farm3.static.flickr.com/2075/2177968086_eac65e5025_o.jpg
The other 3-way CU is for the lights and sockets.
Two questions then really:
a) with apologies for my ignorance, what's the Wylex CU that the Memera one is connected to actually for?
b) is there any way of salvaging what's already there for the shower? I'm guessing not as 45A fuses don't seem to exist for Memera stuff, even if it wasn't stamped 30A - god knows what the wire was in there before! If not, do I need to replace it with something like this?
http://www.screwfix.com/prods/69659...nits/Volex-Shower-Unit-63A-30mA-RCD-1x50A-MCB
And if so, is doing that one of those notifiable things I read so much about on here?
If you need any more info please ask...
Any other useful advice also welcome... cheers!