One cold rad - need some advice...

It would be useful to know if this rad has always been cold since the house was built, or if it started out hot and gradually got worse.

As you have a header tank, and there is at least a bit of flow through that rad when you turn the others off, why not put in a sediment-loosening chemical such as Sentinel X400 and see if the water turns black (which will mean it is starting to loosen old sediment) and run it for 4 weeks before draining?

Or, if you don't want to take up part of the floor, have you considered running a new pipe just above skirting level?

I am not a pro
 