outside socket
15 Jan 2010
Glasgow
Hi , i want to fit a outdoor socket for lawnmower , i was going to take a connection from a socket that has no spur , as the consumer unit has already got RCD ,instead of fitting a 30 amp RCD spur, can i use a 13amp switch instead with the outdoor socket ,or is that not heavy enough ,i like the idea of switching the power to the outdoor socket , what are your thoughts on this
thanks in advance
30 Jun 2009
Londonderry
You can use a switched fuse connection, but you will be restricted to 13A only. Saying that if a standard single socket is being installed, you are restricted to that anyway. If a double gang socket is to be installed, then you would need to assess what the probability is that two appliances are to be used that will exceed the restricted load of 13A at any one given time/period.
Then you also have the option recommended by EFLI
You would still only be able to put a single or double gang socket to this, as it is a unfused spur being used, therefore limited to 20A load on the external socket.
So those are your best options, it could be possible to consider a higher rated two pole isolator, which then would allow two 13A appliances to be used at the same time, although I am not a fan of two 13A appliances loaded on a double gang socket at the same time.
15 Jan 2010
Glasgow
what would be best between ELFIS 20 AMP DP or the switched fuse connection
i would be fitting just a single gang socket for lawnmower & occasional elect drill use
28 Jul 2006
Oxfordshire
Assuming the circuit you are feeding from is a conventional ring-final circuit, protected by a 32A MCB, then the cabling should be in 2.5mm² T&E cable.
28 Jul 2006
Oxfordshire
I would guess so that in the case of a fault developing within it, it can be isolated without having to isolate the whole circuit / all circuits connected to the same RCD?
You could have an isolating switch for everything then. No point for one socket, imo
22 Jan 2012
Jersey
Yes you could, but an outside socket is more at risk I would think, it's waterproof seal could fail or someone accidentally leaves it open one night....
14 Sep 2006
Liverpool
i like the idea of switching the power to the outdoor socket, what are your thoughts on this
Absolutely essential I'd say.
Got a call out late one winter's night, 50-mile round trip. Half of large house with no power. Turned out damp in outside socket ... which only ever got used in the summertime, but had no means of isolation.
Had they been able to switch it off at the end of the summer, it would have saved a lot of inconvenience, and a hefty bill a week before Christmas!
JohnD
Do you accept rounds of applause?
15 Nov 2005
South
Cook Islands
If the socket is outside the house, it would also be possible for a foolish or malicious person to plug in something that tripped the RCD even when the house was unoccupied.
Maybe this would cut power to the burglar alarm or other equipment.
3 Nov 2006
Bedfordshire
People have been known to use their next door's neighbours outdoor socket for zero cost elecricity.
Indoor isolator prevents that.
15 Jan 2010
Glasgow
after reading this comment i'm leaning towards fitting a 13 amp RCD 30ma spur switch ,that way it would trip before the RCD in the main consumer unit if there is ever a problem with water getting into the socket,
a few extra pounds but may be worth it
22 Jan 2012
Jersey
I wouldn't bet on it, either could go first. Stick with a 20amp DP switch of a FCU
