Thank you Mottie and Rob for your help.



All valves open. The boiler has a flow switch, I'll check if it works.All valves open? Invariably the first thing to start in the sequence is the pump, not sure if that particular boiler has a proving switch that then allows the rest of the sequence to activate.



I managed to get the flow switch out.Not sure if that switch can be tested/shorted out
Can you feel the pump running at initial start up, is it actually turning?

Could it be? I have checked the circulation without the boiler for piping from pump to indirect's flow and return and it works fine.Transit bungs left in?

You said in #13 it's for CH onlyI wrote:
Thank you, I am intending to dedicate the boiler to serve the dhw cylinder


I have installed a bi-metallic thermostat on cylinder and wired it on port 96 of the PCB.You need to have a thermostat on the cylinder to control the cylinder HW temps, no other option is acceptable to ensure proper control. That is then just wired in through the SL to the boiler so the stat is in control of the HW