Hi JohnW,
Who told you that?
Because I'm afraid it not the truth!
The use of a fusing factor will simply allow you to absorb a current spike on start up, when over-current protection is to be supplied by a fuse.
If you intend to use a circuit breaker/RCBO to protect a machine with a high starting current, you simply use a C or D Type circuit breaker/RCBO of the same nominal current value.
Simple!
We are talking about over-current protection for general purpose socket outlets, which will be supplying constant steady loads for the next 25 years or so. A faulty appliance drawing 45amps will start to overheat 4mm T&E in 100 seconds (approx), but a 32amp circuit breaker/RCBO will allow this to carry on indefinately. The result will be that the cable will stretch, therefore its' CSA will reduce and its' current carrying capacity will be reduced even further. Use the same faulty appliance again and the cable will be less able to carry the load, become hotter and the problem will begin to spiral, eventually causing fire, accusations of negligence and at worst prosecution for manslaughter!
So exactly who told you this rubbish about current carrying capacity tables being wrong by a factor of 1.45, because if you look back over the history of the regulations it is obvious that this is untrue!
Who told you that?
Because I'm afraid it not the truth!
The use of a fusing factor will simply allow you to absorb a current spike on start up, when over-current protection is to be supplied by a fuse.
If you intend to use a circuit breaker/RCBO to protect a machine with a high starting current, you simply use a C or D Type circuit breaker/RCBO of the same nominal current value.
Simple!
We are talking about over-current protection for general purpose socket outlets, which will be supplying constant steady loads for the next 25 years or so. A faulty appliance drawing 45amps will start to overheat 4mm T&E in 100 seconds (approx), but a 32amp circuit breaker/RCBO will allow this to carry on indefinately. The result will be that the cable will stretch, therefore its' CSA will reduce and its' current carrying capacity will be reduced even further. Use the same faulty appliance again and the cable will be less able to carry the load, become hotter and the problem will begin to spiral, eventually causing fire, accusations of negligence and at worst prosecution for manslaughter!
So exactly who told you this rubbish about current carrying capacity tables being wrong by a factor of 1.45, because if you look back over the history of the regulations it is obvious that this is untrue!