Im a little confused as to what to record for Ze and PFC on a test form:
Its not that Im an idiot or anything its just what is meant to be recorded that gets me so here goes:
When measuring a Ze at origin Im using the meter set to L-PE (3 wire) and I record the result as my Ze value, the meter also displays the PFC value. But of course the PSC L-N should also be tested and the higher of PFC or PSC should be recorded on the test sheet right even though the test sheed says PFC?
Can you confirm that this is the correct procedure.
Its not that Im an idiot or anything its just what is meant to be recorded that gets me so here goes:
When measuring a Ze at origin Im using the meter set to L-PE (3 wire) and I record the result as my Ze value, the meter also displays the PFC value. But of course the PSC L-N should also be tested and the higher of PFC or PSC should be recorded on the test sheet right even though the test sheed says PFC?