YOU CANNOT USE STRAIGHT CONCETRIC and comply to BS7671.

STRAIGHT Concentric stripped.
1247319300.jpg


STRAIGHT Concentric prepped.
1247319301.jpg

Is that just because there's no separate T and N and TN-C is not now allowed?
 
YOU CANNOT USE STRAIGHT CONCETRIC and comply to BS7671.
Is that just because there's no separate T and N and TN-C is not now allowed?
That's part of it - but even if it weren't for that (e.g. if one just wanted to use it as 2-core L+N, with no CPC), the outer conductor is only sheathed (not 'insulated and sheathed') and therefore would not (unless it were in conduit, I suppose) be acceptable for a neutral conductor under BS7671.

Kind Regards, John
 
Well yes, it has no earth, but as said, the neutral is only single insulated by a sheath only.
 
Well yes, it has no earth, but as said, the neutral is only single insulated by a sheath only.
Exactly, and that's why it is not BS7671 compliant (unless in an enclosure/conduit) - in the same way that single-insulated singles are not.

In contrast, split con is no different from T&E - both L and N conductors are 'double insulated'(insulated and sheathed, only the CPC conductors being bare. It can therefore be used anywhere that T&E can be used

Kind Regards, John
 
Well yes, it has no earth, but as said, the neutral is only single insulated by a sheath only.
Exactly, and that's why it is not BS7671 compliant (unless in an enclosure/conduit) - in the same way that single-insulated singles are not.

In contrast, split con is no different from T&E - both L and N conductors are 'double insulated'(insulated and sheathed, only the CPC conductors being bare. It can therefore be used anywhere that T&E can be used

Kind Regards, John

That' what I always say - treat it as T+E.

The benefits it has over T+E are that it can be pulled in far easier, cleated for easier and neater, used externally (where additional mechanical protection is not required), and it's earth is table 54.7 (old 54g) compliant.

It CANNOT be trenched, ducted, or used for 'penetration' protection under BS7671.
 
what I always say - treat it as T+E. The benefits it has over T+E are that it can be pulled in far easier, cleated for easier and neater, used externally (where additional mechanical protection is not required), and it's earth is table 54.7 (old 54g) compliant.
That all sound reasonable - although I'm not sure that there is a compelling reason to say that it is more suitable for external use (where additional mechanicalprotection is not required) than is T&E. Are you suggesting that the nature (material) of the outer sheath of split-con makes it more suitable for external use?
It CANNOT be trenched, ducted, or used for 'penetration' protection under BS7671.
Indeed so, but given that it has no sort of armour, I'm not sure why anyone would think that it could!

Kind Regards, John.
 
Penetration protection as in a nail or screw will always short live to N or E.

It's black sheath is UV stable.
 
Penetration protection as in a nail or screw will always short live to N or E.
"Never say never or always" :-) Penetration resulting in an N/E short without touching L is theoretically possible. Also, if you were very lucky/unlucky, a nail could theoretically pass between the (insulated) N conductors and penetrate L without causing any short (but leaving a live nail)!
It's black sheath is UV stable.
Fair enough - but that's just a question of 'what is available'. T&E could be made with a UV-stable sheath.

Talking of availablility, how readily available is split-con? The likes of TLC and CEF don't seem to offer it.

Kind Regards, John
 
Indeed so, but given that it has no sort of armour, I'm not sure why anyone would think that it could!
Having the live conductors surrounded by earthed metalwork is considered an acceptable means of protection for burried cables. The earthed metalwork does not have to be an armor.

The judgement call that standards writers must make is how to treat neutrals. Neutrals are normally earthed but under certain conditions they can become live. For this reason BS7671 treats the neutral as a "live conductor" though iirc in several places it excepts neutral condutors from rules that apply to other "live conductors".

IIRC under the 16th edition BS7671 did regard split con as a type of cable with protection by earthed metalwork but the 17th edition doesn't. The DNOs regard both straight and split concentric as protected by earthed metalwork.
 
Talking of availablility, how readily available is split-con? The likes of TLC and CEF don't seem to offer it.

Kind Regards, John

Every wholesaler here stocks it in 16 and 25 at least, with many keeping 4 and 10mm too. 35mm is the largest it goes.

The neutrals and earth are so tightly bound tot he live there is no way you would split them to make way for a nail - the insulation on the neutral would be damaged for sure!

The 16th did indeed recognise cables "off concentric construction".

Wholesalers used to also stock the pre-formed stays/dead ends used to aerially suspend the cable without the need of a catenary wire. The manufacturers used to also give you maximum suspended distances. This has now stopped and the manufacturers point you to BS7671 maximum spans.
 
Having the live conductors surrounded by earthed metalwork is considered an acceptable means of protection for burried cables. The earthed metalwork does not have to be an armor.
Fair enough.
The judgement call that standards writers must make is how to treat neutrals. Neutrals are normally earthed but under certain conditions they can become live. For this reason BS7671 treats the neutral as a "live conductor" though iirc in several places it excepts neutral condutors from rules that apply to other "live conductors".
Yes, that's the main issue. However, as I suggested in my last post, I think that there's also an additional issue with split-con due to the fact that the neutral conductors are individually insulated. This creates the possible (albeit very unlikely) scenario of something penentrating the L without coming in contact with neutral (or earth) conductors. Hence, even if I considered neutral to be 'earth', I would therefore personally be rather hesitant to accept something as acceptable 'surrounding earthed metalwork' if that metalwork consisted of individually-insulated strands. However, I can see that there is cope for debate - as you say the DNOs seem happy with both straight-con and split-con.

Kind Regards, John
 
Every wholesaler here stocks it in 16 and 25 at least, with many keeping 4 and 10mm too. 35mm is the largest it goes.
Fair enough. As I say, I've never seen it in a catalogue (on-line or paper), but that doesn't prove much!
The neutrals and earth are so tightly bound tot he live there is no way you would split them to make way for a nail - the insulation on the neutral would be damaged for sure!
I'm sure that's largely true, but still believe in "Never say Never"!

Kind Regards, John
 
That' what I always say - treat it as T+E.

The benefits it has over T+E are that it can be pulled in far easier, cleated for easier and neater, used externally (where additional mechanical protection is not required), and it's earth is table 54.7 (old 54g) compliant.

It CANNOT be trenched, ducted, or used for 'penetration' protection under BS7671.
Looks like it would be a bit of a pig to use for a socket circuit instead of T/E...
 
I think he was talking more in terms of submains and cooker circuits etc rather than a ring, could be wrong though
 
I think he was talking more in terms of submains and cooker circuits etc rather than a ring, could be wrong though
That was certainly my interpretation of what he meant. I feel sure that the disadvantages would outweight the advantages for most socket circuits, even if one could find split-con in small enough CSA.

A more flexible alternative to T&E would, of course, probably often have its attractions.

Kind Regards, John
 