Tested a property today and allot of the zs values exceed the recommended values as per BS7671 calculated at 80%.
The earthing arrangement was TNC-S and the measured ze was 0.36ohms. Which is 0.01 of an ohm above the recommended DNO requirement.
The supply was wired into a 60amp BS1361(fuse) isolator which supplied a 16mm² twin and earth cable that ran about 6metres to a split load consumer unit with 100A main switch for lights and RCD for sockets.
What do people think the best way would be to comply with BS7671?
would it be okay to change the 60amp fused isolator for a 100mA RCD with 63A MCB as running a larger earth to bring down impedance is out of the question. Also, would the RCD need to be time delayed to discriminate for the 30mA?
Any views appreciated.