Plastic overflow as prv discharge from unvented water heater?

Discussion in 'Plumbing and Central Heating' started by neiloneil, 12 Feb 2018.

  1. neiloneil

    neiloneil

    Joined:
    20 Nov 2008
    Messages:
    85
    Thanks Received:
    0
    Location:
    Wiltshire
    Country:
    United Kingdom
    I have fitted a ariston 15litre unvented water heater in an airing cupboard. A shower feed is situated fairly close to the unit, so I am opting to use the full range of expansion controls. Pressure reducing valve, Non return valve, expansion vessel, pressure relief valve, and tundish.
    What I want to know is; Is it absolutely necessary for the prv to discharge through copper pipe?
    The plastic overflow that is existing drops 1 meter straight down, then a shallow fall for another 2 meters where it connects to the kitchen waste outlet pipe The fitting guide says this pipe should be metal, but its going to be a problem getting a new pipe back to the kitchen or to an outside wall.
     
  2. Sponsored Links
  3. Good question but what does the ariston supplied literature say,ave a chat with them.

    Every installation is different o_O
     
  4. John D v2.0

    John D v2.0

    Joined:
    26 Aug 2016
    Messages:
    6,308
    Thanks Received:
    875
    Country:
    United Kingdom
    Yes, plastic melts easily, the water could be super heated water/steam under pressure, need hard metal piping run to a fall into a gulley or somewhere at low level outside.
     
  5. SandyLyon

    SandyLyon

    Joined:
    21 Oct 2012
    Messages:
    625
    Thanks Received:
    140
    Location:
    Lancashire
    Country:
    United Kingdom
    Metal for a reason.
     
  6. Sponsored Links
  7. FiremanT

    FiremanT

    Joined:
    16 Jan 2012
    Messages:
    8,712
    Thanks Received:
    1,710
    Location:
    Uk
    Country:
    United Kingdom
    Not saying you can use plastics, but it won't be under pressure after the tundish
     
    • Thanks Thanks x 1
  8. John D v2.0

    John D v2.0

    Joined:
    26 Aug 2016
    Messages:
    6,308
    Thanks Received:
    875
    Country:
    United Kingdom
    Didn't spot the tundish, thanks
     
  9. neiloneil

    neiloneil

    Joined:
    20 Nov 2008
    Messages:
    85
    Thanks Received:
    0
    Location:
    Wiltshire
    Country:
    United Kingdom
    Thanks for your comments. Because of a lack of route options for getting a 22mm copper pipe to an outside wall, I am now just considering getting a like for like replacement of a direct hot water cylinder and immersion heater. As it does not require a vent pipe, I can use the existing pipework.
     
  10. neiloneil

    neiloneil

    Joined:
    20 Nov 2008
    Messages:
    85
    Thanks Received:
    0
    Location:
    Wiltshire
    Country:
    United Kingdom
    Update..
    I have returned the Ariston 15 litre water heater, and I am now shopping for a direct Fortic cylinder, as it has its own head tank , so venting or discharge is not an issue. I am thinking of an economy 7 type, as I only need the immersion element near the top, otherwise i will be heating up 100 + litres just for kitchen sink and hand basin. Can you suggest any other alternatives please?
     
  11. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page