When plumbers install central heating. Under floor in a customers home and use polyplumb. Do they tend to pressure test or Just fill the system. I know. It says to pressure test to 18bar in polyplumb instructions.
 
Sponsored Links
Joined
8 May 2017
Messages
6,643
Reaction score
1,413
Country
United Kingdom
When plumbers install central heating. Under floor in a customers home and use polyplumb. Do they tend to pressure test or Just fill the system. I know. It says to pressure test to 18bar in polyplumb instructions.
No , a plumber would not likely pressure test a domestic heating system to 18 bar .
Don't know what instructions you are referring to ,but you may have your wires crossed.
Edit. Just read the instructions for polyplumb ( don't use the stuff myself ,would use soldered copper) and it does actually state 18 bar .
 
Last edited:
Joined
4 Oct 2012
Messages
9,118
Reaction score
2,705
Location
East Renfrewshire
Country
United Kingdom
I always fill the system to 2.5 bar and leave it overnight. I just schedule the work during the install so the main pipework with any fittings is all in and can be pressurised and left till the morning. As long as it's still watertight in the morning then I can carry on.

I especially do that with an old open vented system that's being converted.
 
Sponsored Links
Joined
3 Nov 2006
Messages
26,588
Reaction score
2,813
Location
Bedfordshire
Country
United Kingdom
and it does actually state 18 bar

If I was to install a pressurised system then I would test at a pressure equal to the incoming mains pressure to ensure that the pipework would be able to cope with faults that put mains pressure onto the pipe work. ( I do not 100% trust PRVs Regulator or Relief )
 
Joined
21 Oct 2012
Messages
658
Reaction score
144
Location
Lancashire
Country
United Kingdom
The reason polypipe say 18 bar for polyplumb is that is an “O” ring first fitting, this means that when the pipe is inserted into the fitting it passes through the “O” ring first then the “grab ring” second.
If not fully inserted the “O” ring can hold the pipe when the pressure is increased even if the pipe has not passed through the grab ring, hence the 18 bar test. This could result in a full bore blow off.
Grab ring first fittings, like the new Hep2o and polymax only need 1.5 times the working pressure, if they are not pushed fully home they will leak but not blow off.
 
Joined
16 Jul 2009
Messages
761
Reaction score
0
Location
Hull
Country
United Kingdom
The reason polypipe say 18 bar for polyplumb is that is an “O” ring first fitting, this means that when the pipe is inserted into the fitting it passes through the “O” ring first then the “grab ring” second.
If not fully inserted the “O” ring can hold the pipe when the pressure is increased even if the pipe has not passed through the grab ring, hence the 18 bar test. This could result in a full bore blow off.
Grab ring first fittings, like the new Hep2o and polymax only need 1.5 times the working pressure, if they are not pushed fully home they will leak but not blow off.
So as long as pushed all the way home things should be OK?
 
Joined
21 Oct 2012
Messages
658
Reaction score
144
Location
Lancashire
Country
United Kingdom
So as long as pushed all the way home things should be OK?
Good practice is to mark the pipe with the socket depth so you know that the pipe is fully home then pull back on the pipe to ensure the teeth bite, in reality this doesn’t happen.
You can always double check by pushing on the pipe to see if there is any movement but if in full socket you should be fine.
 
Joined
17 Apr 2015
Messages
2,575
Reaction score
409
Location
Warwickshire
Country
United Kingdom
Always wondered if I really needed to pull on the pipe after inserting on push fits, guess that’s a good reason to continue to do so.
 