Interesting reading - @flameport advocating complying with the regs and most others suggesting the regs don’t matter.
Just about sums up the UK these days
The regs do matter, but like all things, common sense is important too.
And we had only TN-S and TT supplies, and we went mad over bonding, and this was reduced, only if we have RCD protection, and the problem is knowing what other trades will do, will they use plastic fittings in bathrooms, or if no RCD use conductive fittings only? Or use links to ensure bonded.For a hundred years, we managed perfectly well without RCD's.
what is the problem with trunking and a surface RCD socket? This was fitted by a scheme member electrician as part of a larger job, and a compliance certificate issued last year. Not the way I would have done it, but can see no real problem with the installation. I would have used an RCD FCU next to the inverter, but the way it has been done, easy to see still active, and easy to reset. So all in all better than using an RCD FCU.The addition of a £20 item so that what you have installed complies with BS7671.Which really would be an entirely pointless exercise, don't you think? A relatively expensive RCD installed, to provide protection to one single socket outlet.
To do that would involve a new consumer unit, which will be at least 20x more than that single RCD for the extra socket. Could easily be a lot more once the existing installation has been properly inspected and tested.Anyone with sense, would make the suggestion of protecting the entire installation, for not much more than the cost of protecting that single socket
The only way for it to be anywhere near the same cost would be for someone to shove an RCD on the whole installation without testing any of it. Not a valid or compliant option and never was.
Quite so. It's perhaps somewhat ironical, even if understandable, that professionals tend to be, or feel, more constrained to abide by rules/regulations, and less able/inclined to apply common sense (assuming they have some), than those who don't suffer fromsuch professional constraints.I agree, that wouldn't be in the pro's interest to do that, but sometimes you have to take a more circumspect view, and assess the risks of simply adding the socket, versus not, or adding the socket, rcbo's, and upset of rewiring for an elderly person. We all know what a professional ought to insist it needs, but this is the real world..
Adding the socket, doesn't make the installation necessarily any less safe. Adding the socket, might mitigate the risk of an elderly person tripping over leads trailed across a floor. Therefore, an overall risk assessment suggests that simply ignoring the rules, and adding the socket, is the safer option, in the circumstances, assuming the OP can install it safely.
When I removed the fuse box's front cover and probed the brass strips going into the box's switch on the right side of box, I found it was still live.
The two wires already in there are the old T&E - ie. made up of several strands of what looks like steel wire twisted together, unlike modern T&E which is just one strand of copper.
I may have committed a mortal sin, but I didn't know what else to do. Instead I put the positive into the 15 amp fuse for the cooker - as it only had a single wire in it and easily accepted the new wire. I put a note in the fuse box cover to warn anyone who works on the box that the double socket in hall is wired into the 15 amp cooker fuse - not the 30 amp ring fuse as would be expected. Also put the same note inside the new socket to warn anyone who works on it in the future.
Note that the new socket will be limited to 15A.UPDATE>>>>>>>
That supplies or did supply something else such as a remote garage, the flat upstairs or whatever.(the unit below the fuse box)
Both have separate connections to the meter, where some incompetent type has shoehorned both tails into the single terminal and attempted to cover up the bodgery with large quantities of tape.
Sorry, maybe my fault, I intended to warn you about the input to the main switch remaining live and quite exposed on those old Wylex boards - just a plastic cap over the screws, if they were fitted. Problem was, the thread got diverted down the road of RCD's.
That, sounds like it was wired in 7/029, tinned copper, or maybe 7/036 aluminium, during the copper crisis.
What's plugged into the cooker circuit right now?
If the socket is supplying a heater or any other high current consuming device while the cooker is turned on the MCB can trip due to a overload. Bear in this mind.
What will the new socket be supplying?
Unrelated to the fusebox above. Both have separate connections to the meter, where some incompetent type has shoehorned both tails into the single terminal and attempted to cover up the bodgery with large quantities of tape.