Johntheo .... thanks for the test suggestions. With the Potterton installed, am getting some strange results.....
Per your test - CH & HW on on controller, HW stat NOT calling, CH stat calling, bolier fires Y valve in mid position. Then turn off HW at controller, CH stat still calling, boiler still firing - so not as you suggested above. Then turn down CH stat, and boiler stops firing.
also tried this if it helps ....
1) Turn CH & HW on on Potterton, both stats set to call for heat = Y valve in mid position - so good
2) With CH & HW still on, turn off HW stat, valve goes to CH position - so good.
3) Turn HW stat back on to call for heat - valve stays in CH position - so NOT good.... not going back to mid position.
4) Turn CH & HW off & then on again to return valve to mid position ... then ....
5) Turn CH stat off and valve goes from mid position to the CH postion --- so NOT good.
6) Turn CH stat back on, valve stays in CH position, despite both stats calling for heat ... so NOT good becaue valve not returning to mid position.
The new valve replaced a Myson which replaced a prior Myson head which went bad. I moved to the DANFOS valve and head because the original Myson valve was stiff and caused the last head replacement to fail after only 18 months or so. Definitely a Y valve with ports A, B and AB. When initially switching both CH & HW on, it goes to mid position and both pipes to cylinder and radiators get hot.