GUYS LOOKING FOR SOMEONE WITH SOME GOOD KNOWLEDGE ON LYNX ELECTRONICS..
Basically we have loads on a local contract and this week alone I have been to 3 seperate boilers that run for a while then stop. they run everytime im there, they run as normal then fail to relight when I leave.
IveREPLACED the SEQUENCE BOARD on 2 and still doing the same so dont want to throw these at them all so lloking for some help.
for the record all stats and thermisters etc run and controls work as normal ??
I know these have an airflow sensor and this part is now obsolete as 1 I was at today kept cutting on/off like a split in a pressure switch hose would do and Potterton call line advised either SEQUENCE Board or Sensor but asI had a new board tried this and still the same... SO NEW BOILER FOR THIS ID SAY
jUst really looking for pointers here as these things are ****ing me off and no real explination for the faults ?? How prone are the airflow sensors to failing ??
The one that was cutting on/off had 2.3 ohm resistance on a steady reading but it either fluxiated now and then to higher or I had a bad connection ( it states it should be between 1.5 and 1.8 )
Im at a loss with these just now and really without spending 2/3 hours a time in a house to get the fault its hopeless...
LYNX ELECTRONIC EXPERTS REQUIRED PLEASE
Basically we have loads on a local contract and this week alone I have been to 3 seperate boilers that run for a while then stop. they run everytime im there, they run as normal then fail to relight when I leave.
IveREPLACED the SEQUENCE BOARD on 2 and still doing the same so dont want to throw these at them all so lloking for some help.
for the record all stats and thermisters etc run and controls work as normal ??
I know these have an airflow sensor and this part is now obsolete as 1 I was at today kept cutting on/off like a split in a pressure switch hose would do and Potterton call line advised either SEQUENCE Board or Sensor but asI had a new board tried this and still the same... SO NEW BOILER FOR THIS ID SAY
jUst really looking for pointers here as these things are ****ing me off and no real explination for the faults ?? How prone are the airflow sensors to failing ??
The one that was cutting on/off had 2.3 ohm resistance on a steady reading but it either fluxiated now and then to higher or I had a bad connection ( it states it should be between 1.5 and 1.8 )
Im at a loss with these just now and really without spending 2/3 hours a time in a house to get the fault its hopeless...
LYNX ELECTRONIC EXPERTS REQUIRED PLEASE