Hello I have a potterton netaheat profile 50e probably about 15 years old this is the first time something has gone wrong!
Whats happens is when I turn on the heating or hot water from the honeywell control pad the fan comes on for about 20 or so seconds and then stops then comes on for 20 second or so then stops. It keeps doing this and obvously I have no hot water or rads working. fortunatly I have hot water through the emersion !
when it used to work the process was fan on .... ignition (ticking noise of spark) then a poof ! noise of the gas lighting and I could see a blue flame through the round glass window
I have changed the fuse in the un switched spur (3amp)
I have tested all the electrical cables with my multi meter all seam ok and fuse on pcb tests ok
I have looked at all the rubber tubes checked for holes or tears all seam ok. I have blown (by mouth) through the tubes and all clear none bent or stopping air flow.
I personally thing it is either the air pressure switch not working properly or pcb needs changing?
So can anyone help me please?
Whats happens is when I turn on the heating or hot water from the honeywell control pad the fan comes on for about 20 or so seconds and then stops then comes on for 20 second or so then stops. It keeps doing this and obvously I have no hot water or rads working. fortunatly I have hot water through the emersion !
when it used to work the process was fan on .... ignition (ticking noise of spark) then a poof ! noise of the gas lighting and I could see a blue flame through the round glass window
I have changed the fuse in the un switched spur (3amp)
I have tested all the electrical cables with my multi meter all seam ok and fuse on pcb tests ok
I have looked at all the rubber tubes checked for holes or tears all seam ok. I have blown (by mouth) through the tubes and all clear none bent or stopping air flow.
I personally thing it is either the air pressure switch not working properly or pcb needs changing?
So can anyone help me please?