Potterton Prima 60F Boiler banging!

Discussion in 'Plumbing and Central Heating' started by dazzystar, 5 Jun 2015.

  1. dazzystar

    dazzystar

    Joined:
    1 Jan 2010
    Messages:
    214
    Thanks Received:
    0
    Location:
    London
    Country:
    United Kingdom
    Hi All,

    I won't bother telling you the whole story but get straight to the point.

    My boiler makes a series of loud bangs which I think are coming from the combustion chamber and after a few of these bangs cuts out.

    Strange thing is that the boiler was on for about an hour then started this behavior, I let it cool down for about an hour and reset it but within a few minutes the bangs were back.

    Any clues?

    Cheers
    Daz
     
  2. Sponsored Links
  3. Razor900

    Razor900

    Joined:
    16 Nov 2007
    Messages:
    6,208
    Thanks Received:
    2,683
    Location:
    Northamptonshire
    Country:
    United Kingdom
    How hot is your pump, can you hear it working?
     
  4. dazzystar

    dazzystar

    Joined:
    1 Jan 2010
    Messages:
    214
    Thanks Received:
    0
    Location:
    London
    Country:
    United Kingdom
    Didn't have time to go upstairs before the boiler banged again and cut out. It's almost as if someone turned the gas down and it was trying to ignite what was there. I could see the boiler casing move slightly as well!

    The gas valve was replaced about a year ago if that helps.
     
  5. Agile

    Agile

    Joined:
    26 Jun 2004
    Messages:
    64,088
    Thanks Received:
    4,604
    Location:
    London
    Country:
    United Kingdom
    We don't give gas/combustion advice here.

    The obvious solution is to check what you can like the pump and isolation valves and any header tank.

    Depending on the type of banging its usually a lack of water causing it to overheat.

    Tony
     
  6. dazzystar

    dazzystar

    Joined:
    1 Jan 2010
    Messages:
    214
    Thanks Received:
    0
    Location:
    London
    Country:
    United Kingdom
    Cheers Tony,

    From your reply I guess you've ruled out a gas valve issue. The plumber who replaced my 2 x two zone valves did shut off some valves when draining the system, etc. Is there a chance they didn't turn on one of them enough?

    He made mention that the balancing valve from the hot water tank was almost fully open and adjusted it.
     
  7. dazzystar

    dazzystar

    Joined:
    1 Jan 2010
    Messages:
    214
    Thanks Received:
    0
    Location:
    London
    Country:
    United Kingdom
    This is probably quite important:

    The boiler has been off for an hour yet I've just been upstairs and the pump is running and boiling hot!

    Both zone valves are closed!
     
  8. Agile

    Agile

    Joined:
    26 Jun 2004
    Messages:
    64,088
    Thanks Received:
    4,604
    Location:
    London
    Country:
    United Kingdom
    Something odd there.

    In most old circuits the pump and boiler are powered by microswitches on the motor valves.

    Modern boilers control the pump to provide over run after boiler use. Where is your pump connected to?

    Tony
     
  9. dazzystar

    dazzystar

    Joined:
    1 Jan 2010
    Messages:
    214
    Thanks Received:
    0
    Location:
    London
    Country:
    United Kingdom
    Pump connected to the boiler. Pump located upstairs with all the other bits including the junction box and programmer (which I've turned off to turn off the pump!)
     
  10. Sponsored Links
  11. Agile

    Agile

    Joined:
    26 Jun 2004
    Messages:
    64,088
    Thanks Received:
    4,604
    Location:
    London
    Country:
    United Kingdom
    You need to monitor the voltage applied to the pump.

    Either its losing the voltage or the pump is sticking and not turning.

    Have you bled water from the pump screw?

    That's assuming this banging is due to lack of flow.

    Tony
     
  12. dazzystar

    dazzystar

    Joined:
    1 Jan 2010
    Messages:
    214
    Thanks Received:
    0
    Location:
    London
    Country:
    United Kingdom
    Hi Tony,

    Can you advise a suitable contact number for you as I think I need to book you!

    Cheers
    Daz
     
  13. steve32

    steve32

    Joined:
    23 Nov 2008
    Messages:
    846
    Thanks Received:
    165
    Location:
    Essex
    Country:
    United Kingdom
    Click on his name and contact details may be in his profile
     
  14. McCombi

    McCombi

    Joined:
    9 Jun 2012
    Messages:
    2,508
    Thanks Received:
    614
    Location:
    Aberdeenshire
    Country:
    United Kingdom
    Plumber has maybe closed bypass when replacing the 2 2 port valves.

    If the pump is wired to the boiler and bouler set for fully pumped, the system needs a bypass before the 2 port valves, or the heat will have nowhere to go to when pump overrun is active after a boiler demand.
     
  15. McCombi

    McCombi

    Joined:
    9 Jun 2012
    Messages:
    2,508
    Thanks Received:
    614
    Location:
    Aberdeenshire
    Country:
    United Kingdom
    Also worth noting that the pump is controlled by a pump over run thermostat in the boiler, it senses the temperature in the boiler, if system is still too hot and pump over run is on, turning off the programmer shouldn't turn pump off, it sounds like the boiler isn't wired correctly, and possibly doesn't have a permanent live and is working off a switched live instead.
     
  16. dazzystar

    dazzystar

    Joined:
    1 Jan 2010
    Messages:
    214
    Thanks Received:
    0
    Location:
    London
    Country:
    United Kingdom
    The boiler stat is at 0 and I turned on the power to the programmer and the pump started to run. No changes to the boilers wiring has been made at all.

    Any idea as to what can cause the pump to be on all the time? The bypass valve is fully open by the way.

    Cheers
     
  17. McCombi

    McCombi

    Joined:
    9 Jun 2012
    Messages:
    2,508
    Thanks Received:
    614
    Location:
    Aberdeenshire
    Country:
    United Kingdom
    The pump should run if pump over run thermostat senses 80degrees or more.

    May be worth checking that it is wired correctly though.
    In wiring centre inside boiler, below control kn
    Should have the pump connected to pump terminals
    A permanent live connected to L
    And switched lives from the 2 ports connected to swl
    And also the neutrals and earth as designated terminals
     