Good, we're getting there!
Ok next thing is to measure the gas rate on CH, that's how much gas is being used. Do it at the meter, as in the FAQ wot I rote. I can't remember the low rate offhand, but it should be a lot lower than the 27kW or so it could be if it's wrong.
Also, if you put the CH on , from cold, how long does it take for the return pipe connection to get very hot, and are any/many of the rads hot at the same time? I'm still suspicious of the flow rate being too low.
If the gas rate is wrong, it's not a diy job - you need the right kit and to know how to use it.