I have a Powermax 155 that appears to lose pressure when we put on the heating or run a bath. If we leave it on just hot water its fine. Any ideas?
 
Sponsored Links
Call in heat team as these are a specialist and potentially dangerous boiler.
 
It might only be a discharged expansion vessel!

Tony
 
Sponsored Links
Some are open vented. All the ones I used to fit were.

I won't go near them for love nor money now :eek:
 
Depress the schraeder valve and as long as water does not come out then repressurise with a car foot pump to about 0.9 Bar ( for a WP of 1.5 bar.

See the FAQ for more details.

Tony
 