Pressure problems

Joined
5 Dec 2009
Messages
1
Reaction score
0
Location
West Midlands
Country
United Kingdom
my ferroli modena 102, started discharging i believe that it was my expansion vessel. i have now installed an external expansion vessel which was working ok until i found a lot of air in one radiator i have since vented the rad and re-pressurised but now the system is getting up to 4 bar and discharging again.

Any ideas
 
Sponsored Links
Check to see if the Filling loop is letting by when closed, disconnect the hose to prove, if pressure rises with hose dissed suspect HW Plate Heat Exchanger (primary/secondary water mixing) ;)
 
what size expansion vessel did you fit? did you fit it on the return? and what pressure is the external expansion vessel charged too?
 