PRV Gave it a twist to left but still losing water

Joined
27 Nov 2013
Messages
300
Reaction score
2
Location
Yorkshire
Country
United Kingdom
Hi all,

My boiler wont start, I noticed sometimes not all the time water outside, so I gave the PRV a nudge to left held it and heard some water release and the presuure dropped and also heard some gargling...I now have the pressure drop everyday to 0 even when I put it to 1 bar. Can the PRV stop the boiler kicking in? do I need a new one? I do notice if the bolier does start I usually hear a small gargle of water then bingo it starts...is this the PRV thats blocked?

many thanks
Dan
 
Sponsored Links
I am this week mate I just wanted to see if anyone could suggest the problem for reference, would it make a gargle noise when the bolier kicks in normally?
 
Once the pressure drops to below a certain limit, the boiler will not fire, it's a safety feature. If there is water seeping out from the external pipe from the PRV then it is letting by. Will need looked at or replaced. The gurgling noise will be the boiler pressurising again after the water has been evacuated by the PRV, it's a usual occurrence.

Time for an engineer as Gav suggests.
 