...Only trouble is that at 8kg/m2, I make this 0.078kN/m2, where as you list this as 0.087kN. Could this be a typing error?
It was the chipboard that I did not understand John, bur after a lot of thought realised where I was going wrong. To the best of my knowledge MD chipboard weighs in at 625kg/m3, therefore 1metre square of 18mm = 0.111kN/m2. Slightly different to yours.. Perhaps I have not got the cube weight right?...
Just a couple of points to finish this off.
Actually, I made a slight error when I said BS648 gives plasterboard as 0.87. In fact that comes from manufacturers spec. so there might be small differences between manufacturers. The small difference in your calculations (i.e. 8kg = 0.078kN) comes about because you are using 9.82 as the factor for gravity whereas I normally just use 10. So Lafarge 12.5 at 8.7kg/m² becomes 0.087kN. And hotrod is right. The figures are given as a range ( I don't know why either?) and I just use the upper figure.
In reality it is daft to design joists on such tight tolerances and I don't defend it myself. I was really just pointing out to the OP that if he went back to his struct engineer to complain he would probably just say that his calcs are technically correct and the problem stems from the builder altering the design.
I would support your earlier post about 'I' joists. I've been using them for years now and although a bit more expensive the advantages significantly outweigh the extra cost.
If I do specify timber joists I err on the high side. Not necessarily for structural reasons but because the stiffer floor will be quieter. In my experience people are far more likely to complain about a creaky floor than anything else.