That's not right - unless I'm going crackers too - static/standing pressure would usually always be higher and when the outlets are opened the pressure would usually drop, if anything, certainly wouldn't expect it to rise.I wasn't expecting the dynamic pressure to increase, so I did it twice in case I was going crackers, results the same both times. I did notice the outside tap appears to be leaking a little bit from the gland when its on, whether this would have any effect on the pressure, I don't know.
Also dynamic flow of 9.75 L/min with a dynamic pressure @ 3 bar wouldn't be expected either. With a 3 bar dynamic pressure I would expect a much higher flow rate than that.
Are those figures with the pipework as is and not been corrected?