I have come across problems with EICR's in the past where the inspector has given the circuit a code but I can't see why the code has been given. Code 2 - 415.1.1 is great even if it should not have been code 2 at least you know why it has failed.
The same with comments on the forum not permitted - 522.6.6 OK we all know the reason why and we can give why we feel it's not permitted.
No it doesn't. How did you comply with Part 6?
At least does show where he is looking and quite valid a plug in EZ150 tester only shows better than 1.50Ω and so does not give a 100% answer as to if it passes. Can't remember new limit for a ring final but not talking about a ring final and 16A spur is around the 2.73Ω mark so good enough.
OK the 40 mS tripping time needs a special meter but he did say except for RCD testing. What we must remember is enquiry is a permitted method so to get some one else to test and then use those results on the paper work you have raised is permitted.
I see nothing wrong in getting an EICR done then copying the test results onto an EIC and signing it. Neither is there anything wrong with using a three signature form.
As to LABC accepting the paperwork I will agree I did myself have problems. But the Liverpool inspector was very helpful and the Cheshire one was not too bad it was only the Flintshire one who raised objections. It does vary council to council and not even sure if notifiable anyway.
We have argued again and again as to what is a new circuit. Until some one is taken to court we do not have the answer. It would seem adding a FCU does not make a new circuit under Part P but it does with BS7671 so if adding a FCU does not form a new circuit then why would adding a MCB form a new circuit they both do the same thing after all.
If I was asked is it a new circuit if so you need to pay £5 I would say yes it's a new circuit, but if they want £100 then I would answer no it's not a new circuit as I would not want to pay £100 for a rubber stamp. And until the minimum charge is dropped to a reasonable figure I am sure most people who would need to register the work with the LABC would say the same until a test case shows other wise which is unlikely to happen with owner occupied property.
Most houses today have two circuits (RCD is a over current device) which are further split into more circuits (MCB's) but with a populated CU non of those circuits will be new.
Yes I will agree this is not what was intended by the law but it will require case law to clarify. If the house was being rented out then I would not take a chance we have seen how courts are very quick to find land lords guilty so the tenant can claim compensation.
The Mrs Whittall case is a good example. But for owner occupier DIY I know of no cases where the grieving husband has been taken to court for killing his wife.
Since he was able to show a reasonable drawing and work out he has a TN-C-S supply I would not class Jackson as an idiot and if we expect every regulations to be followed both in spirit and word then may as well get rid of the Electrics UK section of DIYNOT.