radiator hot at bottom but doesn't bleed

Joined
11 Apr 2004
Messages
121
Reaction score
2
Country
United Kingdom
The radiator hot at bottom but cold at the top, when I undo bleed screw no air comes out.

Any ideas.

Thanks
 
Sponsored Links
What type of system do you have?
 
Sponsored Links
Sort of. Is there anywhere you need to add pressure?
 
No. Boiler has no options for adding. It’s a Veissman
 
is it a 100 Vitodens Compact? With no pressure gauge? And are the radiators relatively old? and is there a small (1ft x 1ft x 2ft) water tank in the loft, with a ball float like in a traditional WC cistern? How deep is the water in it? How deep is the layer of mud?
 
If the system is full then maybe the air bleeder is blocked, remove bleeder and push a pin or thin wire in to clear it.
 
is it a 100 Vitodens Compact? With no pressure gauge? And are the radiators relatively old? and is there a small (1ft x 1ft x 2ft) water tank in the loft, with a ball float like in a traditional WC cistern? How deep is the water in it? How deep is the layer of mud?
Have to check that tomorrow, it’s in not easy to get to. Thanks
 
If the system is full then maybe the air bleeder is blocked, remove bleeder and push a pin or thin wire in to clear it.
I have removed the whole nut and nothing happens, no air escapes.
 
If there is water in the expansion tank then you probably have a blocked cold feed meaning that water can't get into the heating system. Usually the problem is sorted by chopping out and replacing the cold feed/vent connection.
 
Have you checked the water level in the small f&e tank ,(probably in the loft )?
 