Just had a problem trying to connect a ring final to a MK RCBO. No matter how tight the screw it would not grip 2 X 2.5mm cables. Has anyone else had this problem and if so, how did you rectify it?
... is that not the very arrangement in which, if they are fractionally different in size, it becomes difficult to grip all of them adequately? Allowing as much separation as one can get between the conductors may help - since the movable part of the cage can then 'tilt' slightly in order to adequately grip conductors of fractionally different sizes.Also stand your cables like soldiers. i.e. in a line, next to each other.

They are nominally the same size, but the real world being the real world, there is likely to be a fractional difference - particularly after the cables have been handled, stripped, bent etc. (and certainly after the initial attempt to clamp them in a terminal).But these are the same size. Am I missing something?
They are nominally the same size, but the real world being the real world, there is likely to be a fractional difference - particularly after the cables have been handled, stripped, bent etc. (and certainly after the initial attempt to clamp them in a terminal).But these are the same size. Am I missing something?
If the moveable part of the cage couldn't tilt at all, it would have to compress the (fractionally) fatter conductor to exactly the same size as the (fractionally) thinner one before it could grip both simultaneously and equally. As I said, there presumably always is a little 'tilt' avaialble', and the benefit of that will, I would have thought, theoretically be at its greatest when the two conductoirs are as far apart as possible.
Kind Regards, John
If you are referring to 'traditional' terminals, in which one tightens a screw directly onto the conductor(s), then I think that's probably even worse (than 'cage' or 'bar' terminals), particularly when one is trying to terminate two or more conductors in the same terminal.If all that stuff is right, why don't they make round tunnel terminals like older consumer units had?
Yes, that makes sense. However, the problem the OP described is not (at least, IME) unique to RCBOs - I've experienced it (with multiple conductors) with other things that use bar/cage clamps (including MCBs), even when one has a good view of what one is doing. Have you not?I think the only problem with RCBOs is the depth of the terminals and therefore the difficulty of positioning one wire on each side of the clamp without being able to see where they are. In fact they seem deeper than they appear. Even if the conductors do seem tight they may only be held where one conductor has crossed the other.
Not really.I've experienced it (with multiple conductors) with other things that use bar/cage clamps (including MCBs), even when one has a good view of what one is doing. Have you not?
Sure - but two is obviously common. When I wrote 'multiple', I meant 'more than one' (and most commonly two). More than two (which I agree is rare, but not unknown) presumably magnifies the potential problem being discussed.Not really. It's rare to have more than two conductors in one clamp, isn't it?
Swings and roundabouts there, I reckon. As I said before, a little tilting (or twisting or bending) of the clamp might actually facilitate better tightening onto both of two conductors.If the clamp twists or bends to accommodate the wires then obviously one could remain 'looser'.