RCBOs - OK to shorten the N tail?

Joined
9 Nov 2013
Messages
422
Reaction score
33
Location
Aberdeenshire
Country
United Kingdom
Hi,

Quick question. Is it OK to shorten the Neutral tails on RCBOs to keep the wiring neat? There are two reasons why I'm wondering, firstly I seem to remember reading somewhere that they shouldn't be shortened. The other reason is that they have a nice bootlace ferrule crimped on the end of the tail which would be a bit pointless if the lead's going to be cut down to length.

Same regarding the earth lead I suppose, which again is miles longer than needed although not so bulky so less of a problem.

Thanks in advance, Tony S
 
Sponsored Links
Yes they can be shortened PROVIDED the end is fitted with the correct size of boot lace ferrule and then the correct tool is used to crimp the ferrule.
 
I do cut mine to length but crimp on a new bootlace ferrule. The neutral is usually a multi-strand tri-rated cable and its the only way to ensure all of the strands get terminated.

PS You'll invalidate the warranty if you chop it though...
 
Sponsored Links
Thanks everyone. By the way I just nipped out and had another look in the panel. The first RCBO, installed by the sparky when the supply was connected, has had the N tail shortened and no ferrule fitted. The multicores are just all connected into the terminal. I'll crimp that one along with my additions.

Tony S
 