Say you had a dual RCD CU.


You had a 63A RCD fitted, and for the sake of argument you had 3x32A MCB's connected to that RCD.

Say a cooker, hob and ring.

Main fuse probably 60A.

I assume that is ok? As in practice the ring isn't going to be drawing much current and the cookers not at maxiumum load.

Thank you
 
An old rule of thumb that DNO sparks use for diversity is add up all your protection devices and multiply that by 0.4. That will give you a rough guide to how much loading you will use. It's not a definate design formula but as a guide it's pretty good

The 3 x 32amps sound fine. If you think that a cooker range with a combined hob/oven in one unit could be fitted on a 32amp protection device on it's own as they often are. So I would think you are ok there
 
You wouldn't normally do sub divisions of the installation like that. But as I said it's a good rule of thumb for an installation and you could class your 63amp RCD as a sub division so 38amps seems about right.
 