RCD as sole protection for shower unit

Joined
11 Jan 2004
Messages
45,987
Reaction score
3,560
Country
United Kingdom
A colleague rang me today to ask whether an RCD on its own was considered satisfactory protection for an electric shower.

I can't find the regs number..... :cry:
 
I hope there was some form of overcurrent provided to the circuit :shock:

As I'm sure you're aware an RCD will not operate on overload or a staight L-N fault.
 
No there wasn't!!

Yes I am!!

But I can't find the reg now....I'll give up soon & go to beddy-byes... :wink:
 
431-01-01 Except where the overcurrent is limited [by the nature of the supply] every live conductor shall be protected by one or more devices for automatic interruption of the supply in the event of overload current [and] fault current...
 
No, no. You misunderstand!!

He was querying an existing install he had been called out to work on... :wink:
 