when doing an rcd full auto tesy should the cream functional earth be dissconnected I get a fail on half load :?:
 
No, the functional earth lead should not be disconnected.
The RCD should be tested in isolation i.e. with the final circuits not connected.
If it still fails then the RCD is over sensitive and should be replaced.
 