To add to the topic.
For TT installations, where there is a main time delayed RCD (with typical EF trip currents of 100 to 500mA), in addition to another downstream (say 30mA EF trip current for sockets etc), it is necessary to ensure time discrimination.
A 3:1 discrimination ratio is required between the two RCD's that are connected in series, and this must be verified before testing.
It means that the delayed RCD must have an operating current at least three times that of the non-delayed type. For example, to discriminate properly with a 30 mA device, a second connected on the supply side would need to have an operating current of at least 90 mA (in practice, a 100 mA RCD is likely to be used).
The test for the time-delayed RCD consists of applying 100% of the normal rated current, when the device should trip within the time range of:
50% of rated time delay plus 200 ms, and
100% of rated time delay plus 200 ms.
For example, an RCD with a rated tripping time of 300 ms should trip within a time range of:
(150 + 200) ms = 350 ms and
(300 + 200) ms = 500 ms