RCD Tripping out

Joined
23 Apr 2005
Messages
53
Reaction score
0
Location
Bournemouth
Country
United Kingdom
I was undertaking eath loop impedance tests on my sockets today, and the RCD keeps tripping out before I can get a reading.

Any ideas? how I can get my readings

Cheers
 
Sponsored Links
Buy a meter with a D-Lok.

Or, Use the R1 + R2 method after the RCD, and add this to the EFL before the RCD.
 
A D-Lock is that the meters with the ring at the top?

and what is EFL

Soz, bit confused
Thanks tho
 
D Lok: An earth fault loop impedance tester which can measure with a reduced current which does not trip RCDs.

Just out of interest, are you actually using an earth fault loop impedance tester?

EFL = Earth Fault Loop (Impedance),
 
Sponsored Links
Anymore other ways just for future reference. By the way I'm on my second year... and I like to be able to know how to solve a problem before I encounter one.

Thanks in advance
 
You could bypass the rcd, either by moving the circuit under test onto the otherside of the cu, or otherwise, then take your reading, and put it back, but this is frowned upon, because the circuit is energised without the rcd protection that has been fitted to it, but under controlled conditions (you know for certain the circuit won't be used, and I suppose, that the RCD is not providing the only means of protection against indirect contact (so not on a TT system)) then I suppose it could be used...
 