Renovating a room that has 2 light switches, no earths

Discussion in 'Electrics UK' started by jonbey, 15 Jul 2020.

  1. jonbey

    jonbey

    Joined:
    17 May 2012
    Messages:
    5,429
    Thanks Received:
    301
    Country:
    United Kingdom
    Renovating a room and it had 2 light switches, both were housed back to back on a now removed partition in a wooden box. There is no earth cable. All other rooms have earth, I think - our bedroom certainly does. All other switches look newer and the ones I've removed have metal back boxes.

    I have bought new back boxes and switches to go on the new stud wall I'll build. Can I use these same lighting cables as they are, or should I put in an earth? If I put in an earth, can I run a separate cable from another light fitting in the loft, or should I run new cables?

    The switches are currently hanging down in the photo - I've put them out of reach of short people and got a sensor bulb in there at the moment so no need to touch them while working in the room.

    IMG_20200713_224924326.jpg

    IMG_20200715_174005471.jpg

    In the loft above

    IMG_20200624_205711587.jpg
     
  2. Sponsored Links
  3. ericmark

    ericmark

    Joined:
    27 Jan 2008
    Messages:
    16,462
    Thanks Received:
    1,487
    Location:
    Llanfair Caereinion, Nr Welshpool
    Country:
    United Kingdom
    official following regulations or being safe is not quite the same, if the home is to be rented then it has to follow current regulations, but if owner occupied then some common sense is required. The problem with no earth is it limited what can be used, plastic switches with either plastic screws or caps that fit over the screws, and to be frank if it were me I would want to rewire so I am not restrained as to what I can use latter.

    The guy rewiring my mothers house use three core and earth for every switch, but did not connect the third core, it was left for me to either use for two way lighting or a neutral.
     
  4. RF Lighting

    RF Lighting

    Joined:
    31 Mar 2006
    Messages:
    19,618
    Thanks Received:
    1,297
    Location:
    Leeds
    Country:
    United Kingdom
    Those cables are at least 60 years old now, so I think you’ve had your money’s worth out of them.

    If you replace the cables you know for certain that they are going to be good and not need replacement for another 60+ years, and it’s going to be a 1000 times easier to do it now while your room is in busts than it will be once it’s all put back together and decorated nicely.

    It’s a no brainier for me.

    You must test the earth wires at your junction box to prove they are actually earthed before you go connecting onto them.
     
  5. jonbey

    jonbey

    Joined:
    17 May 2012
    Messages:
    5,429
    Thanks Received:
    301
    Country:
    United Kingdom
    OK, so in the room on one side is this

    IMG_20191027_215934565.jpg

    So connecting to earth should be easy, if I knew what I was going or where these wires are going in the loft ...

    In fact, there's a light in the loft too - could I come off this? That would be easier...
     
  6. jonbey

    jonbey

    Joined:
    17 May 2012
    Messages:
    5,429
    Thanks Received:
    301
    Country:
    United Kingdom
    Think i might have just keep one of my good ideas....

    This is the old part of the house. 2 years ago i had an extension, with new consumer unit split into 2 halves, one for old, one for new. So new light circuit is on its own circuit. There are just 5 lights inside, plus 4 outside lights.

    So can i run a cable from one of the new ceiling roses? Any one, or does it have to be last one?
     
  7. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    33,987
    Thanks Received:
    3,724
    Location:
    Retired to:
    Country:
    Portugal
    Any one, it doesn't have to be the last one.
     
    • Like Like x 1
  8. Sponsored Links
  9. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    19,621
    Thanks Received:
    1,994
    Location:
    Oxfordshire
    Country:
    United Kingdom
    Just test to make sure that the earth you are connecting to actually is an earth.
     
  10. jonbey

    jonbey

    Joined:
    17 May 2012
    Messages:
    5,429
    Thanks Received:
    301
    Country:
    United Kingdom
    How do I do that?
     
  11. jonbey

    jonbey

    Joined:
    17 May 2012
    Messages:
    5,429
    Thanks Received:
    301
    Country:
    United Kingdom
    Nearest new light fitting on new consumer unit looks like this:

    IMG_20200716_134056108.jpg

    So I assume that the main lighting cable runs to the switch first (3 switches for the 3 ceiling lights in the kitchen).

    So, I can't hook up a cable onto this can I, as this is either on or off from switch? Or have I misunderstood it?
     
  12. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    33,987
    Thanks Received:
    3,724
    Location:
    Retired to:
    Country:
    Portugal
    You will need a long piece of wire to verify continuity between the CPC(earth wire) and the Main Earthing Terminal near or in the consumer unit.
     
  13. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    33,987
    Thanks Received:
    3,724
    Location:
    Retired to:
    Country:
    Portugal
    That is correct.

    You will have to run the new cable from a switch.
     
  14. jonbey

    jonbey

    Joined:
    17 May 2012
    Messages:
    5,429
    Thanks Received:
    301
    Country:
    United Kingdom
    Damn. Switch in nice new wall. That's that plan blown!

    Maybe I should just bite the bullet and start a new light circuit for the old house .... as well as this room + corridor, I have another bathroom, and hallway still to renovate. If I use ceiling rose junctions (is that the right term?) then I could add the bedrooms later...

    New circuits on the left, old on the right. I think 18 might be the external light I had put in separately after extension.