replace 32A MCB with 6A/20A in ex-cooker circuit?

Joined
8 Feb 2017
Messages
1
Reaction score
0
Location
Bishop's Stortford
Country
United Kingdom
I recently had a new, more powerful cooker installed (including new wiring) which is protected by a 40A MCB in the Consumer Unit.

The CU still has the previous 32A MCB in place, which used to protect the previous cooker. The wire used here is 6mm2. In the kitchen this wire spurs off to supply a double socket. 2.5mm2 wires are used for this spur. This spur is now and will continue to be the only electrical outlet for this circuit, which is protected by a 32A MCB.

Am I right in thinking that the 32A MCB has now become inappropriate for this circuit? Should I replace it with a 6A MCB, or due to 6mm2 cable with 20A MCB?
 
Sponsored Links
No need to change anything. The spur will be protected by the fuses in the plugs as long as you don't add any more sockets to it.

If you do then replace the MCB with 20A or 25A one, OR
replace the cable with 4mm².
 