I have bought a new built in oven to replace my old one and I'd like to confirm a few things before I start.
The old oven was wired directly to a cooker control unit, which has an additional 13A socket. This was hard wired to a 32A MCB on the consumer unit using 6mm flex. I want to replace like for like using the 13A socket for the hob ignition.
The installation instructions do not quote the power output, but it does state that the oven must be protected with a fuse between 15A and 20A. It also says that the oven requires 2.5mm flex to the cooker control unit.
Is my current setup suitable to wire the new oven without changes? I am concerned that the control unit/MCB combination does not provide adequate rating.
Cheers
The old oven was wired directly to a cooker control unit, which has an additional 13A socket. This was hard wired to a 32A MCB on the consumer unit using 6mm flex. I want to replace like for like using the 13A socket for the hob ignition.
The installation instructions do not quote the power output, but it does state that the oven must be protected with a fuse between 15A and 20A. It also says that the oven requires 2.5mm flex to the cooker control unit.
Is my current setup suitable to wire the new oven without changes? I am concerned that the control unit/MCB combination does not provide adequate rating.
Cheers