Replaced EP2002 with Hive dual active heating but now ...........

Joined
8 Apr 2021
Messages
3
Reaction score
0
Country
United Kingdom
In Sept 2020 I replaced a Potterton EP2002 programmer controlling a fully pumped system with Hive Dual Active. First photo shows EP2002 wiring and 2nd Hive wiring.
Screenshot 2021-04-08 at 17.54.56.png
Screenshot 2021-04-08 at 17.53.03.png

What I did

1. Removed red bridge wire between EP L and 5 – not required as is built into Hive already.

2. Blue, blue sleeved with red + black wires in EP N joined in a choc bloc – NOT connected elsewhere.

3. Red wire originally in EP L plus the “non-bridge” wire in 5 connected together to Hive L

4. Yellow sleeved with red wire originally in EP 4 connected to Hive terminal 4

5. All earths joined in choc bloc & connected to Hive earth terminal (not metal back box)

Everything worked when commissioned - first time and worked faultlessly until 8th Jan 2021, when, although Hive receiver called for heat (i.e. bottom green CH LED was lit) boiler did not ignite. Managed to restart it eventually by turning off power (at fused spur) the back on and boiler lit.

It was indicative of a zone valve issue from 2013 - replaced V4034 Feb.

But same thing has happened again 6 to 8 times before end of March 2021.

Baxi sent an engineer but he said that as there were no lights on the boiler at all (fault LEDs) he knew it wasn't the boiler. He did not check anything. Boiler is due it's 3rd service 15th April.

Have redone all connections with Wago lever connectors with single wire to Hive terminals incl the 2 reds in L (now only single wire)

Anyone come across this before please?

G
 
Baxi sent an engineer but he said that as there were no lights on the boiler at all (fault LEDs) he knew it wasn't the boiler. He did not check anything. Boiler is due it's 3rd service 15th April.
baxi will only work on the boiler, and a service wont find your problem, what were the two wires in A on the EP connected to, it is just a parking terminal but what did you do with the two wires ?
 
Well spotted Ian - I have missed out that the two wires (blue sleeved red and brown) that were in A were simply joined together in a choc bloc but not to anything else. Replicates "parked in A" doesn't it?

G
 
Last edited:
Well spotted Ian - I have missed out that the two wires (blue sleeved red and brown) that were in A were simply joined together in a choc bloc but not to anything else. Replicates "parked in A" doesn't it?

G
yes they were parked in A but what was at the other end ?
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top