Repressurising Greenstar 24i junior condensing combi boiler

Discussion in 'Plumbing and Central Heating' started by Luckat, 20 Aug 2019.

  1. Luckat

    Luckat

    Joined:
    20 Aug 2019
    Messages:
    6
    Thanks Received:
    0
    Country:
    United Kingdom
    Hi,

    Partner and I have just got back from holiday to find our hot water and heating isn't working on the Greenstar 24i junior combo boiler. Cannot contact our landlord today (need hot water to wash up and shower) we're pretty certain the problem is the pressure on the boiler as it's at low.

    We watched the Worcester video on repressurising and the key is nowhere to be found and there are no holes to insert the key on the bottom of the boiler (please find pictures attached)



    Leads me to believe there is another way to repressurise the boiler we just can't figure it out. Any help would be immensely appreciated!

    Thank you!

    Lucy
     
  2. martyndc88

    martyndc88

    Joined:
    26 Apr 2009
    Messages:
    451
    Thanks Received:
    39
    Location:
    South Glamorgan
    Country:
    United Kingdom
    You're looking for a braided silver hose connecting two pipes from the boiler together. They'll have valves on them
     
  3. Luckat

    Luckat

    Joined:
    20 Aug 2019
    Messages:
    6
    Thanks Received:
    0
    Country:
    United Kingdom
    Hi,No

    Thanks but there isn't a silver braided pipe anywhere on the bottom of the boiler. We've only got copped pipes...could it be one of those?

     
  4. martyndc88

    martyndc88

    Joined:
    26 Apr 2009
    Messages:
    451
    Thanks Received:
    39
    Location:
    South Glamorgan
    Country:
    United Kingdom
    Take a picture of the pipes underneath the boiler
     
  5. Luckat

    Luckat

    Joined:
    20 Aug 2019
    Messages:
    6
    Thanks Received:
    0
    Country:
    United Kingdom
    Hi,

    Is this clear enough?

    Thanks
     

    Attached Files:

  6. martyndc88

    martyndc88

    Joined:
    26 Apr 2009
    Messages:
    451
    Thanks Received:
    39
    Location:
    South Glamorgan
    Country:
    United Kingdom
    No a front on view of the pipes. I don't want to see the underneath of the boiler
     
  7. Luckat

    Luckat

    Joined:
    20 Aug 2019
    Messages:
    6
    Thanks Received:
    0
    Country:
    United Kingdom
    Tap directly above the blue pipe does nothing except dribble water when opened, so is not the keyless repressurising lever.
     

    Attached Files:

  8. martyndc88

    martyndc88

    Joined:
    26 Apr 2009
    Messages:
    451
    Thanks Received:
    39
    Location:
    South Glamorgan
    Country:
    United Kingdom
    The two valves with the brass blank ends on need to be connected with a hose and then you can top the pressure up
     
    • Like Like x 2
  9. dannymassive

    dannymassive

    Joined:
    24 Nov 2017
    Messages:
    29
    Thanks Received:
    4
    Location:
    Torbay, Devon
    Country:
    United Kingdom
    Also, the brass cap on the pipe with the blue pipe connecting has a drip coming out of it - could be where your pressure has been going if that is a constant drip. Might be worth checking
     
  10. mrStat

    mrStat

    Joined:
    11 Mar 2017
    Messages:
    174
    Thanks Received:
    63
    Location:
    Hertfordshire
    Country:
    United Kingdom
    As @martyndc88 said, you need to join the two red circled pipes together with a filling loop (silver braided hose) to fill the boiler.

    Hopefully the hose is tucked on top of the boiler or somewhere where you can get to it. You will need a spanner to undertake the job.

    @dannymassive the one with the drip is their cold mains, won’t affect pressure loss on the heating side, however the OP may get a bit wet when that brass cap is removed.
     

    Attached Files:

  11. dannymassive

    dannymassive

    Joined:
    24 Nov 2017
    Messages:
    29
    Thanks Received:
    4
    Location:
    Torbay, Devon
    Country:
    United Kingdom
    @mrStat Well spotted, I don't know why I mentioned the pressure loss as it's bimmin' obvious that it's the cold feed!! #facepalm! Brass cap still looks like is dripping though?!
     
  12. Luckat

    Luckat

    Joined:
    20 Aug 2019
    Messages:
    6
    Thanks Received:
    0
    Country:
    United Kingdom
    Hi everyone,

    Thank you so much for all your answers!

    Couldn't find a pipe so went a bought one from screw fix - next question - which end goes on which pipe? One end of the hose has a black on/off tap and the other doesn't!

    Thanks,

    Lucy
     
  13. dannymassive

    dannymassive

    Joined:
    24 Nov 2017
    Messages:
    29
    Thanks Received:
    4
    Location:
    Torbay, Devon
    Country:
    United Kingdom
    Looks like there is an isolation valve on the far end pipe which will need opening with a flat head screw driver - once the filling loop pipe is connected. Then you can turn the black plastic tap until the pressure is at the correct level. Then turn off the tap, close the isolation valve and remove the filling loop.
     
  14. Luckat

    Luckat

    Joined:
    20 Aug 2019
    Messages:
    6
    Thanks Received:
    0
    Country:
    United Kingdom
    Hi everyone,

    We managed to repressurise the boiler finally so thank you so much for all your help, definitely couldn't have done it without you! :)

    Lucy
     