Actually, today you could have a 32A ring with an MCB and 1.5mm² cable but it is just specifically 'not allowed'.
IIRC 1.5mm is permitted in MICC?
Did an EICR on Monday where someone had taken this to the extreme, every room (although supplied by ring finals) had sockets supplied from at least two circuits, some rooms had 3 or 4 circuits in them. Nightmare to test
I was explaining the electrical principles and rules behind ring circuits to topgazza.
Is saying "you could do something but it's not allowed" suggesting he have it?
There is nothing electrically non-compliant about a 32A / 1.5mm² ring circuit apart from the fact that it is specifically forbidden.
Yes, but not talking about that.IIRC 1.5mm is permitted in MICC?
It complies with all the criteria, but -But why ? if it is, (according to you) not electrically non compliant
433.1.204 states a ring shall have conductors of minimum csa of 2.5mm² (except micc).Interested to know why it's forbidden? If as you say, "There is nothing electrically non-compliant" …….
Indeed, and there seem to be a couple of things about that for which I struggle to think of an electrical reason ....It complies with all the criteria, but - 433.1.204 states a ring shall have conductors of minimum csa of 2.5mm² (except micc).
Secondly, if (despite my 'struggling') there is some rational electrical reason for 1.5mm² not being acceptable, why does this not also apply to MICC?
Kind REgards, John
Well, yes, one might suspect something like that because of the nature of MICC.Possibly something heat or fire rated,which micc would not suffer from
How long do the labels last?
Possibility I suppose, although once you've worked out which circuit it is to isolate & remove, the label inside is redundantSeveral years so far ... If you don't want to label the front of the sockets then at least label inside the backboxes.