Riello condencing boiler

Joined
12 Jul 2024
Messages
3
Reaction score
0
Country
Ireland
Hi

My boiler starts and stops after about 10 seconds. The reason for this is likely to be that the oil ran out.

Is there anything I can do as a quick fix?
Boiler was installed about 3 or 4 years ago.

Thanks with any help

D
 
First dip tank to check you actually have run out of kero.
If tank empty get it filled then carefully bleed out air .
Don't keep pressing reset good way to cause damage.
 
We would always disconnect flexi oil line as it goes into pump and run a decent amount of kero into a container.
There should be a shut of valve in or very near boiler.
 