Sure, but you seem to be concerned about 'breaking capacities' - and if the fault current is anywhere near that, it will trip very rapidly. Even if (as you have in places) one talks about a downstream device of only 1 kA breaking capacity, a fault current approaching 1 kA would trip your hypothesised C50 MCB (let alone a B50) very rapidly.The upstream device only helps us if it trips rapidly.
See above.What we want to avoid is leaving a "gap" where the fault current is high enough to overwhelm the downstream protective device, but not high enough to rapidly trip the upstream one..
In any event, there is surely only an issue to discuss if the plug fuse has a lower breaking capacity than some upstream protective device (which, is rarely, if ever, going to be the case in domestic installations when the fuse is {as it nearly always will be} a BS1362 one). If the breaking capacity of the plug fuse is at least as great as the PFC, that alone presumably satisfies protection requirements downstream of the socket, the upstream device only being relevant to the protection of the cable between CU and socket?
In terms of BS1363, I'm only familiar with BS1363-1 and BS1363-2, and BS1363-1 only refers to use of BS1362 fuses. I would therefore have to do a bit of reading to determine what it has to say about things other than BS1363-1 plugs (with BS1362 fuses) plugged into a BS1363-2 socket.It's weird that BS1363 apparently specified a high breaking capacity fuse for plugs, but allowed a much lower breaking capacity one for adapters, and afaict says nothing at all about protection inside wall-warts leaving those up to IEC standards (which I suspect are based on the assumption of some reasonable upstream fuse, given that most of the world doesn't have fused plugs). ... But I guess that is how the standard's sausage is made.