Should not be less than 2.5mm² in flat twin+earth, other factors such as cable length and how it is installed need to be taken into consideration.
 
The cable must be rated at 66% of the breaker rateing for the way its installed, usually 2.5mm² cable is used for a 32A ring (any other rating would be a non standard arrangement) but depending on how the cable is run, you might in a few cases need 4mm²
 