50 m2 floor area is it? I looked glanced at a 20+ year old copy I happened to have nearby.
Even so, far more options with a ring.
Even so, far more options with a ring.
It is indeed, but I'm surprised to hear that it was ever as low as 20m²50 m2 floor area is it? I looked glanced at a 20+ year old copy I happened to have nearby.
One size rarely fits all - IMO, both probably have their places.Even so, far more options with a ring.
It's a bit more than 75mm²It USED to be 50 m2 for an A2 circuit (30 or 32 amp in 4.0 mm2), so again, a significant difference to today's 75 mm2.
Indeed - although, as I've pointed out,the OSG figure for an A3 is now 50m².Not being awkward - genuinely don't understand. sparkwright wrote: A 20 amp radial in 2.5 mm2 should only serve a 20 m 2 area.
I've always taken it to mean the floor areas of rooms/places (including halls/landings etc.) in which there were sockets supplied by the circuit. I don't think it's anything to do with the cable length, which is why I keep saying that cable length/VD has to be considered as a separate (and quite possibly the limiting) issue. In other words, as far as the OSG's 'floor area guidance' is concerned (but not VD considerations) it's OK to have an A3 providing sockets in room(s) with a total floor area ≤50m², even if it's 100m from the CU, and passes through umpteen rooms and spaces (with large floor areas) on the way.What does serve mean in this context?
That makes some sense - although, even then, it was probably a bit silly to have a 'floor area rule' which didn't take the nature of rooms into account.I gather the floor area measurement is something to with the use of electric fires, which was common when the ruling first came out. I believe it was worked out so there weren't too many electric fires on one circuit. It is a bit of a pointless rule now.
True - it would be an iterative process.It looks as if your list may need a little re-ordering, and other attention. It would be quite difficult to 'work out the CCC of the cable' before one had 'picked a cable size'. However, merely swapping (3) and (4) would introduce other anomalies - so a general re-think may perhaps be needed.3. Work out the current carrying capacity of the cable, given the Installation Method, and any other applicable derating factors, as per Appendix 4.
4. Pick a cable size that's OK for voltage drop and complies with Ib ≤ In ≤ Iz as per Section 433.
Kind Regards, John
75mm²?It USED to be 50 m2 for an A2 circuit (30 or 32 amp in 4.0 mm2), so again, a significant difference to today's 75 mm2.
I being the person responsible for the Design, Construction, Inspection & Testing of the electrical installation (as indicated by my signature below), particulars of which are described above, having exercised reasonable skill and care when carrying out the Design, Construction, Inspection & Testing, hereby CERTIFY that the said work for which I have been responsible is to the best of my knowledge and belief in accordance with BS 7671:2008, amended to 2011 except for the departures, if any, detailed as follows.Interesting answers. Never crossed my mind that rings weren't the obvious choice. My question was really about how to run 2.5 cable that wouldn't have heat problems with the insulation board.
If you do something other than what you said you'll do, or allowed them to think you'll do, then rocks and hard places will make an appearance instead of a Completion Certificate...When you applied for Building Regulations approval, what did you say, or by default/tacit acceptance agree, would be the way that you would ensure the work complies with Part P?
Indeed:75mm²?It USED to be 50 m2 for an A2 circuit (30 or 32 amp in 4.0 mm2), so again, a significant difference to today's 75 mm2.
It's a bit more than 75mm²