I'd like to have 2 sockets (switched from a grid switch) vertically aligned with each other, maybe a couple of feet apart.
Is it safe and within regs to run the cable of the upper one through the metal back box of the first? In one instance the first box reached would be the cooker plate with 6mm cable.
Also, can I safely run 2x (or more?) 2.5mm T&E cables through a 20mm or 25mm metal conduit? Or even a 6mm cooker cable and a 2.5mm?
Thanks,
Robert
Is it safe and within regs to run the cable of the upper one through the metal back box of the first? In one instance the first box reached would be the cooker plate with 6mm cable.
Also, can I safely run 2x (or more?) 2.5mm T&E cables through a 20mm or 25mm metal conduit? Or even a 6mm cooker cable and a 2.5mm?
Thanks,