S plan no hot water fault diagnosis.

Joined
22 Nov 2009
Messages
2,956
Reaction score
762
Location
Oldham
Country
United Kingdom
Is there a guide anywhere? Cylinder is a megaflo.

Heating fine, everything was switched off for a week while away but made hot water fine when switched back on on Friday evening, the RCD tripped on the circuit the boiler is on yesterday but reset straight away (I suspected washing machine at the time as it's on its way out) so it it could be related but can't remember if water was timed on at the time, I don't know whether we have had hot water since then as cylinder is quite big so didn't run out till this morning.

Programmer has power so should I start at the wiring centre, cylinder stat or straight to messing with lever on valve?

Thanks
 
Sponsored Links
1. The cylinder is unvented, so the motorised valve on the coil is part of the safety system. Should only be touched by someone with current G3 qualification.
2. These normally have one or two immersion heaters fitted. The top one should give you a limited amount of hot water if on.
3. With respect to the boiler hot water side, if you have a multi-meter, know how to use it and are comfortable working with mains voltage electricity you could test for 230V at appropriate points.
4. If it turns out to be the motorised valve not opening, or not firing the boiler, get a G3 registered engineer to replace it.
 
Check if the overheat thermostat on your HW cylinder has tripped, and press it in to reset if needed, this closes the motorised valve when it trips
 
Sponsored Links
Thanks, it was the motor on the valve, more a case of spotting the scorch marks backed up by a bit of metering than following a sequence. Fortunately I had a spare Honeywell valve and the motors were a straight swap.

IMG_20210606_155349309.jpg
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back